消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

汽车库车辆如何疏散?

地下汽车库都有划分多个防火分区,防火分区之间采用防火墙和防火卷帘门进行分隔,汽车库发生火灾时,联动状态下卷帘门都是降下来的,那么车辆如何疏散,如何确定车辆的疏散出口。

liu_sir | 2024-10-16 19:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 8

张治福 2024-10-17 08:42 00 [回复]举报

就怕你进去开车,把人也搭进去了

一个呆呀 2024-10-17 08:50 00 [回复]举报

问的太好了!

规范首要考虑了人的生命安全问题,财产保全是次要问题

消防资源网 2024-10-17 08:51 00 [回复]举报

4.6.3 疏散通道上设置的防火卷帘的联动控制设计,应符合下列规定:
   1 联动控制方式,防火分区内任两只独立的感烟火灾探测器或任一只专门用于联动防火卷帘的感烟火灾探测器的报警信号应联动控制防火卷帘下降至距楼板面1.8m处;任一只专门用于联动防火卷帘的感温火灾探测器的报警信号应联动控制防火卷帘下降到楼板面;在卷帘的任一侧距卷帘纵深0.5m~5m内应设置不少于2只专门用于联动防火卷帘的感温火灾探测器。
   2 手动控制方式,应由防火卷帘两侧设置的手动控制按钮控制防火卷帘的升降。

阳明心 2024-10-17 08:52 00 [回复]举报

1,疏散通道的卷帘分两步下降,留有一定的供车辆疏散的时间

2. 人员可以通过疏散楼梯疏散

我头发贼黑 2024-10-17 10:47 00 [回复]举报

问下擎天柱,他们听到警报自己会跑

wetom 2024-10-21 09:27 00 [回复]举报

以前,有观点认为汽车库卷帘门两部降是预留汽车疏散的,后来规范组解释疏散仅是人员的疏散,不考虑汽车的疏散,所以,我们这边目前验收地下车库都要求一步降了。所以呢,期待新车库规吧。

shwbest 2024-12-02 15:25 00 [回复]举报

着火时不考虑车辆疏散,只考虑人员疏散。

消防网友67503 2024-12-10 16:41 00 [回复]举报

规范要求设置人员疏散出口,每个防火分区不少于两个

关闭

关闭

手机APP下载