成品粮仓库内需要设置消火栓吗

成品粮仓库内需要设置消火栓吗

啊张 | 2024-09-06 16:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

我头发贼黑 2024-09-07 08:30 00 [回复]举报

不设置,粮食平房仓设计规范 GB50320-2014 7.0.1 散装粮食平房仓内不应设消防给水设施,其他粮食平房仓内不宜设消防给水设施;仓外应设消防给水设施。

花生12138 2024-09-07 09:13 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)8.2.2 本规范第8.2.1条未规定的建筑或场所和符合本规范第8.2.1条规定的下列建筑或场所,可不设置室内消火栓系统,但宜设置消防软管卷盘或轻便消防水龙:3 粮食仓库、金库、远离城镇且无人值班的独立建筑。,应该是不用设的

周家斌 2024-09-07 10:06 00 [回复]举报

不需要,也不能要。