火灾报警控制器的显示时间与实际时间应不超过多长时间,有规范要求吗

火灾报警控制器的显示时间与实际时间应不超过多长时间,有规范要求吗

地精修补匠 | 2024-09-03 10:38
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

张治福 2024-09-03 17:51 10 [回复]举报

针对火灾报警控制器产品,老规范要求的是日计时误差不大于30S。

在2025年即将实施的《火灾报警控制器 GB4717-2024》中,日计时误差不大于6S

地精修补匠   回复: 张治福2024-09-04 11:49

十分感谢