消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下车库,室内覆盖系统机房,固定通信机房,宏蜂窝基站机房,π接室,强弱电间等电气设备间超50平米,给排水不做气灭,是否需要做排烟?

地下车库,室内覆盖系统机房,固定通信机房,宏蜂窝基站机房,π接室,强弱电间等电气设备间超50平米且无外窗,给排水不做气灭,是否需要做排烟?

Da_n_dAN | 2024-08-15 10:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

懒得说 2024-08-16 09:03 00 [回复]举报

需要做防排烟,不要纠结

周家斌 2024-08-16 11:48 00 [回复]举报

看能否定性无可燃物?是否经常有人停留?,规范条文有口!

布泽德 2024-08-17 09:51 00 [回复]举报

这些机房都是有很多可燃物,且在地下室,需要做防排烟

潘天坤 2024-09-12 15:54 00 [回复]举报

楼上几位老师解释的很清楚

是否需要排烟,一般考虑“场所定性”、“建筑面积”、“经常有人停留”、“可燃物较多”

如果都不属于,那么可以不设置排烟设施,当然设置洞口、百叶让房间达到非密闭也是可以的

关闭

关闭

手机APP下载