消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

高位水箱间需要设置消防电话分机吗?

高位水箱间需要设置消防电话分机吗?哪一条规范有要求?

小甜甜$$ | 2024-04-19 10:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

南明离火 2024-04-19 16:27 10 [回复]举报

不用,没有

ligang-xiao 2024-04-20 10:11 20 [回复]举报

规范中没有明确要求,根据个人经验理解,高位消防水箱间应该是不需要的,高位消防水箱间一般作用是确保消防管网似应状态下系统压力,火灾时基本没啥用。实际中,高位消防水箱间,基本也没有看到安装消防分机电话。但有的专家老师可能会让设置,一些企业为了避免麻烦就安装了,也没多少钱。


6.7.4 电话分机或电话插孔的设置,应符合下列规定:   

1.消防水泵房、发电机房、配变电室、计算机网络机房、主要通风和空调机房、防排烟机房、灭火控制系统操作装置处或控制室、企业消防站、消防值班室、总调度室、消防电梯机房及其他与消防联动控制有关的且经常有人值班的机房应设置消防专用电话分机。消防专用电话分机,应固定安装在明显且便于使用的部位,并应有区别于普通电话的标识。    

2.设有手动火灾报警按钮或消火栓按钮等处,宜设置电话插孔,并宜选择带有电话插孔的手动火灾报警按钮。    

3. 各避难层应每隔 20m 设置一个消防专用电话分机或电话插孔。    

4.电话插孔在墙上安装时,其底边距地面高度宜为 1.3m~1.5m 。

关闭

关闭

手机APP下载