消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

气体灭火事故排风与消防排烟:气体灭火防护区没有事故排风口,但有排烟口,把排烟口改成事故排风口符合要求吗了

气体灭火防护区没有事故排风口,但有排烟口,把排烟口改成事故排风口符合要求吗了

消防网友17819 | 2024-03-08 14:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

南明离火 2024-03-09 08:51 00 [回复]举报

距地300mm设置事故排烟口

手持一消板砖的小白 2024-04-28 16:01 00 [回复]举报

应该是不可以的 ,事故排风口一般在下,排烟口在上。另外气体灭火的原理是窒息,浸渍,不需要排烟。因此可以把上方的排烟口,下引到距地面0.5米以下就可以了。同时还要满足喷洒时关闭排烟(风)口。

wbsyz   回复: 手持一消板砖的小白2024-09-01 11:35

防火阀在火灾联动时会关闭,灭火后需要打开排风,这个防火阀地面执行机构需要设置在防护区外吗

0    0 [回复]举报

潘天坤 2024-06-29 23:15 00 [回复]举报

当设置在灭火剂释放前必须关闭通风系统、防护区开口的气体灭火系统时,可以将排烟系统改为气体灭火后的机械排风(事故通风),但是注意气体灭火后的机械排风应设置在防护区的下部

同时当设置排烟系统 (包括自然排烟系统和机械排烟系统)时,不应采用火灾自动报警系统联动启动的方式自动开启系统排烟,以保证灭火系统实施有效灭火

建筑防火通用规范条文说明提及:对于建筑中上述需要设置排烟系统的场所,当设置气体灭火系统等在灭火剂释放前必须关闭通风系统、防护区开口的灭火系统时,允许将排烟系统改为事故通风系统,当设置排烟系统 (包括自然排烟系统和机械排烟系统)时,不应采用火灾自动报警系统联动启动的方式自动开启系统排烟,以保证灭火系统实施有效灭火

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载