消防应急照明灯具是否每个单独房间都要安装?

有一些办公室面积比较大,是否需要每个单独房间都设置应急照明和安全出口标识

消防网友63108 | 2023-12-14 14:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

安洪全 2023-12-14 16:20 01 [回复]举报

每个都需要

我的是昵称 2023-12-15 13:21 00 [回复]举报

按规范建筑设计防火规范 GB50016-2014(2018年版) >来说,不需要。

10.3.1 除建筑高度小于27m的住宅建筑外,民用建筑、厂房和丙类仓库的下列部位应设置疏散照明:     1 封闭楼梯间、防烟楼梯间及其前室、消防电梯间的前室或合用前室、避难走道、避难层(间);     2 观众厅、展览厅、多功能厅和建筑面积大于200m²的营业厅、餐厅、演播室等人员密集的场所;     3 建筑面积大于100m²的地下或半地下公共活动场所;     4 公共建筑内的疏散走道;     5 人员密集的厂房内的生产场所及疏散走道。

办公室不属于人密场所,如果是有办公属性的会议室要设。再说了,应急照明是疏散逃生用的,是设在疏散通道,前室和楼梯间的。

       房间疏散门不用安全出口标识。办公室大了,人可以用疏散指示标志。安全出口标志是在前室入口或楼梯间入口处相对安全的地方用的。



消防网友63108   回复: 我的是昵称2023-12-18 15:21

感谢

1    0 [回复]举报

大司马 2023-12-15 15:53 00 [回复]举报

问题不够准确,不一定,实际执行过程中 你可以参考一下规范中的情况2,如果大于200平米就可以考虑设置了


疏散可以参考:

除建筑高度小于27m的住宅建筑外,民用建筑、厂房和丙类仓库的下列部位应设置疏散照明:     1 封闭楼梯间、防烟楼梯间及其前室、消防电梯间的前室或合用前室、避难走道、避难层(间);     2 观众厅、展览厅、多功能厅和建筑面积大于200m²的营业厅、餐厅、演播室等人员密集的场所;     3 建筑面积大于100m²的地下或半地下公共活动场所;     4 公共建筑内的疏散走道;     5 人员密集的厂房内的生产场所及疏散走

尤里奥洛夫 2023-12-17 21:30 00 [回复]举报

公共建筑就需要