消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

应急照明配电箱是否可以设置在丙类仓库内?

《建筑设计防火规范》10.2.5 可燃材料仓库内宜使用低温照明灯具,并应对灯具的发热部件采取隔热等防火措施,不应使用卤钨灯等高温照明灯具。
  配电箱及开关应设置在仓库外。应急照明配电箱不能设置在丙类仓库的原因是什么呢?是为了方便控制呢,还是怕引起火灾呢?

dreamoflove | 2023-12-07 15:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-12-07 15:53 10 [回复]举报

怕引起火灾,规范要求属于是控制引火源。

山屈 2023-12-07 17:42 30 [回复]举报

1、问题中的10.2.5,规范条文解释说明:本条是根据仓库防火安全管理的需要而作的规定。
2、《消防应急照明和疏散指示系统技术标准 GB51309-2018》3.3.7应急照明配电箱的设置应符合下列规定:1)宜设置于值班室、设备机房、配电间或电气竖井内。(按功率规定设置具体位置)
3、《民用建筑电气设计标准 GB51348-2019》13.7.15消防应急照明电源供电应符合下列规定:1、……为疏散照明供电的双电源自动转换箱、配电箱和EPS箱应安装于防火分区的配电小间内或电气竖井。
理解:一是防止配电箱、电池等故障或发热成为火源;二是库房等区域设有喷淋设施,非集中电源应急照明220V供电,集中电源应急照明220V转36/24V,消防双电源持续工作,火灾时喷淋动作可能造成电击事故;三是应急照明为确保应急情况下人员的疏散照明,应更长时间工作,配电箱在库内如短时间内被火烧坏,将影响整个应急照明系统的应急工作。

阳明心 2023-12-08 08:40 00 [回复]举报

二方面的原因兼而有之。

关闭

关闭

手机APP下载