消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防电梯内专用电话

您好,我想问一下,规范里要求消防电梯内应设置与消防控制室直接联系的专用电话,这里边说的是指五方对讲也可以,还是必须单独设置消防分机电话

王宇晗 | 2023-12-04 10:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-12-04 12:07 00 [回复]举报

单独设置消防分机电话

消防设备的线路从材质到敷设都有特殊要求,五方对讲平时能满足功能上的要求,但是火灾发生时的使用不可靠

王宇晗   回复: 安洪全2023-12-04 16:51

好的,谢谢,平时我们也是这么要求的 但是就是没有明确规范说是消防分机电话,所有有时候挺被动的

0    0 [回复]举报

安洪全   回复: 王宇晗2023-12-05 08:42

规范要求的不太明显,可能是比较细节的分项。

也向您学习,把细节做好,为项目负责。

0    0 [回复]举报

关闭

关闭

手机APP下载