LNG气化站储罐冷却喷淋系统的消防主泵是电泵,备用泵必须用柴油机泵吗?备用泵可以用电泵吗?

LNG气化站储罐冷却喷淋系统的消防主泵是电泵,备用泵必须用柴油机泵吗?备用泵可以用电泵吗?

冬天的太阳 | 2023-10-27 09:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

充楞装傻 2023-10-27 15:56 00 [回复]举报

一组消防水泵可由同一消防给水系统的工作泵和备用泵组成。

消防给水同一泵组的消防水泵型号宜一致;

我的是昵称 2023-10-30 14:49 00 [回复]举报

是否用柴油机泵主要的条件之一就是你的消防用电等级是几级。如果是一级或二级,而你的消防用电不能达到要求,那么必须用柴油机泵或发电机。

冬天的太阳   回复: 我的是昵称2023-11-16 16:02

消防用电等级是二级,已具备市电和柴油发电机供电,这种情况下的备用泵还必须采用柴油机泵吗?

0    0 [回复]举报

我的是昵称   回复: 冬天的太阳2023-11-17 09:05

备用泵是在主泵故障后转换为备泵。和发电机没有关系。发电机是消防应急备用电源。主备泵都是要用发电机的。