消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防爆墙可以开孔吗

防爆墙上面是否可以开泄压口?有什么规范依据?

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

黄辉 2021-01-14 15:29 00 [回复]举报

找了几个规范,供您参考。


 特种气体系统工程技术标准 GB50646-2020


7.2.4 有爆炸危险的特种气体间与无爆炸危险房间之间,应采用耐火极限不低于4.00h的不燃烧体防爆墙分隔,防爆墙上不应开设门窗洞口;设置双门斗相通时,门应错位布置,门应为甲级防火门。



锂离子电池工厂设计标准 GB51377-2019 

6.2.6 有爆炸危险的区域与相邻区域应采用耐火极限不低于3.00h的不燃烧体防爆墙分隔,防爆墙上不得开设门窗洞口;设置门斗相通时,门应错位布置,门斗的隔墙应为耐火极限不低于2.00h的防火隔墙,门应采用甲级防火门。

关闭

关闭

手机APP下载