消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

求教830平方电竞酒店防火门需要安装吗,相关规定是啥

我场所在建筑地上2层,经营为电竞酒店,有两个疏散楼梯,楼梯口需要安装防火门吗,需要安装几级的,是消防法律法规那一条,求教,感谢各位老师回答

阿白_qB1r | 2023-04-04 22:26
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防网友62482 2023-04-05 02:39 00 [回复]举报

830平方电竟酒店地上两层建筑面积不超1500平方耐火等级为三级。据建筑防火通用规范
5.3.3 除本规范第5.3.1条、第5.3.2条规定的建筑外,下列民用建筑的耐火等级不应低于三级:
1 城市和镇中心区内的民用建筑;
6.4.3 除建筑直通室外和屋面的门可采普通门外,下列部位的门的耐火性能不应低于乙级防火门的要求,且其中建筑高度大于100m的建筑相应部位的门应为甲级防火门:
1 甲、乙类厂房,多层丙类厂房,人员密集的公共建筑和其他高层工业与民用建筑中封闭楼梯间的门
6 歌舞娱乐放映游艺场所中的房间疏散门

消防网友62482 2023-04-05 03:22 00 [回复]举报

两层歌舞娱乐场所楼梯间为封闭楼梯间。要安装防火门。防火门为乙级防火门。

依据防火通用规范。6.4.3(1,6)。

消防黄河 2023-04-05 09:22 10 [回复]举报

多层酒店应设置封闭楼梯间,设置乙级防火门。建规:5.5.13 下列多层公共建筑的疏散楼梯,除与敞开式外廊直接相连的楼梯间外,均应采用封闭楼梯间:       1 医疗建筑、旅馆及类似使用功能的建筑;

隔壁老丁 2023-04-16 15:20 00 [回复]举报

5.5.13 下列多层公共建筑的疏散楼梯,除与敞开式外廊直接相连的楼梯间外,均应采用封闭楼梯间:       1 医疗建筑、旅馆及类似使用功能的建筑;       2 设置歌舞娱乐放映游艺场所的建筑;(建筑设计防火规范)

现在很多地方将电竞酒店视为歌舞娱乐场所,严格来说你房间门都要采用乙级门的;

关闭

关闭

手机APP下载