防火卷帘需要防护冷却系统吗

普通的钢质防火卷帘需要装防护冷却系统进行降温保护吗,具体规范在哪

| 2022-07-27 08:18
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防黄河 2022-07-27 10:14 20 [回复]举报

 当防火卷帘的耐火极限仅符合现行国家标准《门和卷帘的耐火试验方法》GB/T 7633有关耐火完整性的判定条件时,应设置自动喷水灭火系统保护。自动喷水灭火系统的设计应符合现行国家标准《自动喷水灭火系统设计规范》GB 50084的规定,但火灾延续时间不应小于该防火卷帘的耐火极限。建规6.5.3

  回复: 消防黄河2022-08-10 13:45

非常感谢

0    0 [回复]举报

周家斌 2022-07-27 17:13 10 [回复]举报

需要隔热性能的就需要,

  回复: 周家斌2022-08-10 13:45

非常感谢

0    0 [回复]举报