消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟风速问题

  假设现在有A 、B  、C、  D共 4个防烟分区,均为机械排烟,如果只是A着火,只有A排烟口打开吸烟,但是我的风机是按照相邻两个防烟分区风量最大之和计算的风量选取的,还加了1.2倍系数;所以,当A着火时候,因为只有A的口打开了,A的风管和风口风速岂不是超了规范值了?请问大家指教!!!

苏莱曼 | 2022-04-27 16:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防网友73006 2022-04-28 19:00 00 [回复]举报

所有的风口截面积都是计算得出的,喉口风速不会大于10m/s

夏日么么凉 2022-06-02 16:06 00 [回复]举报

加风量调节阀

关闭

关闭

手机APP下载