消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

走道排烟问题

房子正南正北坐落,一共三层,单面有房间的走道,2-3层走道两端有窗,1-3层走道北侧有6个窗,一层走道两端为疏散门,一层房间均不大于100平,二至三层走道东侧均有一个大于100平的会议室,其他房间均不大于100平米,且均有外窗,请问这种情况大于20米长的走道排烟我应该走道两端分别设置2㎡排烟窗并保证排烟窗间距不小于走道长度的2/3,还是按照走道面积2%平均设置在走道所有外窗上?

小设计人 | 2022-04-10 16:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

充楞装傻 2022-04-11 09:05 00 [回复]举报

   3 当公共建筑仅需在走道或回廊设置排烟时,其机械排烟量不应小于13000m³/h,或在走道两端(侧)均设置面积不小于2㎡的自然排烟窗(口)且两侧自然排烟窗(口)的距离不应小于走道长度的2/3。
    4 当公共建筑房间内与走道或回廊均需设置排烟时,其走道或回廊的机械排烟量可按60 m³/ (h·㎡)计算且不小于13000m³/h,或设置有效面积不小于走道、回廊建筑面积2%的自然排烟窗(口)。

1F可用第3款;

2F~3F用第4款;

100平会议室也是2%;


十万嬉皮 2022-04-11 10:12 00 [回复]举报

按照规范要求肯定是适用于走道两端两个平方的。我个人理解可以适用百分之2。你也可以人为制造极端设计,比如打通两个房间,扩大房间的火灾危险性,使房间的面积超过100平方米,这样就适用于烟规的走道和房间都需要考虑排烟的情况了,这个时候就又可以使用百分之2了。 但是要注意开窗面积及开窗高度  自然排烟窗要设置在储烟仓里面。       烟规真是扯淡

消防网友78337 2022-04-11 13:21 00 [回复]举报

烟规4.6.3

说的很清楚

3 当公共建筑仅需在走道或回廊设置排烟时,其机械排烟量不应小于13000m³/h,或在走道两端(侧)均设置面积不小于2㎡的自然排烟窗(口)且两侧自然排烟窗(口)的距离不应小于走道长度的2/3。    

4 当公共建筑房间内与走道或回廊均需设置排烟时,其走道或回廊的机械排烟量可按60 m³/ (h·㎡)计算且不小于13000m³/h,或设置有效面积不小于走道、回廊建筑面积2%的自然排烟窗(口)。


你属于情况4,房间也需要排烟,按面积2%计算,

虽然按4的计算,开窗面积可能算的很小,但是房间排烟量计算和防烟分区划分,开窗高度都需要考虑了。

关闭

关闭

手机APP下载