消防给水系统有要用稳压泵稳压,用主泵稳压可以吗?

消防给水系统有要用稳压泵稳压,用主泵稳压可以吗?

远古鱼龙 | 2022-02-24 13:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

沐浴阳光 2022-02-24 13:30 20 [回复]举报

    不能用主泵稳压,稳压泵有自动启动和停止功能,而消防泵不允许自动停泵。

远古鱼龙   回复: 沐浴阳光2022-02-24 16:08

化工企业要求压力较高!属于稳高压系统,稳压泵达不到要求的压力怎么办?此套系统有6个主电动消防泵,两个稳压泵

0    0 [回复]举报

刘丽波   回复: 远古鱼龙2022-02-25 08:47

设稳压泵的目的就是防止主泵频繁启动,且主泵不能随便停泵。不知稳压泵是那种情况的选不到,是图集上没有吗?最近做了个自动消防炮系统,就是稳压设备图集上选不到型号。稳压泵和稳压罐是否可以单独给参数配置。

1    0 [回复]举报

远古鱼龙   回复: 刘丽波2022-03-01 08:28

规范上没有明确稳压要用稳压泵还是主泵,所以现在有两种说法:一、要用稳压泵稳压,这样可以减轻消防管网压力,管道不容易老化漏水。二、只能用主泵稳压,才能保证消防管网压力,稳压泵压力只是按漏水量设计,完全不能保证消防用水的压力。我们该怎么正确选择?