消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

工业建筑内的柴油发电机房消防设施

建规5.4.13:布置在民用建筑内的柴油发电机房应符合下列规定,那么工业建筑内的柴油发电机房是否同样适用呢?

汤工 | 2022-01-23 20:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

ROY 2022-01-26 13:44 00 [回复]举报

可能算不上答案,简单说说看法,如有错误欢迎指正。

检索了非常多有关柴油发电机房消防设施配置要求的资料,全部都指向了民用建筑。但是民用建筑的规范直接套用在工业建筑上,可以做参考,不完全适用。

检索了遇到过的工业厂房设计,在某动力供应站内配置5台柴油发电机,使用水喷雾灭火系统保护柴油发电机区域。此建筑火灾危险性被定义为丁类,但是柴油发电机所在建筑,在民用建筑内最低也应界定为丙类。以上情况可供参考。

关闭

关闭

手机APP下载