消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防系统主泵可否用自吸泵

 遇到一项目,做地下消防数水池,地上消防泵。常规选用长轴液下泵,轴流深井泵,甲方非要用自吸泵,不知道可不可以?

画图匠 | 2021-07-08 17:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

刘丽波 2021-07-08 19:07 00 [回复]举报

消防要求选用自灌吸水的,自吸泵不可以

画图匠   回复: 刘丽波2021-07-09 09:16

那请问老师,当自吸泵入口设置地上水罐,液位高于水泵叶轮中心线时,这种可不可以认为也是自灌式吸水呢?

0    0 [回复]举报

刘丽波   回复: 画图匠2021-07-10 11:40

消防泵要求全程自灌吸水,因为备用泵不知何时启动,启动时水位要满足自灌条件。

1    0 [回复]举报

画图匠   回复: 一二一2021-07-13 15:07

可能我没表述清楚,泵入口地上水罐为负压水罐,开始用水罐内的水灌泵,运行起来水罐形成负压将地下消防水池的水再吸上来,起到引水的作用,水池内的水也是可以都利用的。这种情况呢?

0    0 [回复]举报

画图匠   回复: 刘丽波2021-07-13 15:18

就类似这种进口自带饮水箱的,在满足启泵时间的前提下,也是不可用的吗?

0    0 [回复]举报

乌伤浪人   回复: 画图匠2022-04-17 23:57

消规规定不允许。按你的截图搞的太复杂了,为什么不采用消规允许的轴流深井泵呢?你只有与甲方多解释了,否则从设计院角度就不能出图。

0    0 [回复]举报

关闭

关闭

手机APP下载