消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵房,消防控制室备用照明

消防水泵房,控制室等设备用房要求设置正常照度的备用照明,但是条文解释又说应急照明。到底是应急照明等多设置几个,达到规定的照度即可,还是要专门拉一条备用照明线。

消防网友31154 | 2025-03-19 21:15
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

消防龙一条 2025-03-20 08:40 01 [回复]举报

有正常照明和应急照明就行,没要求必须另外单独拉一条备用照明,当然这样做也没问题。

潘天坤 2025-03-20 09:00 00 [回复]举报

消防控制室、消防水泵房、自备发电机房、配电室、防排烟机房等消防设备用房应设置备用照明

发生火灾时仍需工作、值守的消防设备房(例如消防控制室、消防水泵房、自备发电机房等)应设置疏散照明

备用照明和疏散照明不一样,是两种东西,不能互相替代



董付秋 2025-03-20 09:04 00 [回复]举报

备用照明是在未发生火灾(火情)时消防水泵房的正常照明停电(或故障)使用的照明设施;应急照明是发生火灾后自动转换成的工作状态。备用照明与正常照明、应急照明的电源不同。

水清云淡 2025-03-20 14:06 00 [回复]举报

现在一个项目就是设置有管员的AC220V照明灯具接入水泵控制柜,灯具要求 带电池,另外又设置了疏散指示牌和壁灯电源是DC36V的,这个是不是既设置了备用照明又设置了应急照明呢

潘天坤   回复: 水清云淡2025-03-20 15:00

双电源箱的出线回路接普通照明线路,这是备用照明

普通照明加蓄电池可以理解为过渡照明

不确定您描述的“疏散指示牌和壁灯电源是DC36V”是否为“疏散照明和疏散指示标志”,从规范来说发生火灾时仍需工作、值守的消防水泵房应设置“疏散照明和疏散指示标志”


0    0 [回复]举报

关闭

关闭

手机APP下载