消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外地下式消火栓问题

北方冻土深度深,室外地下式消火栓栓口距地面200~400mm,泄水阀应在冻土深度以下,栓口与泄水阀中间需加设法兰接管,图集上说法兰接管为厂家供货范围,但是咨询厂家不生产该连接管,施工单位说自己也加工不了,法兰和消火栓的对不上,还有中间还有一个启闭的传动杆需要加长。请问各位大神是否遇到此问题,如何解决的?

拾青 | 2024-12-25 19:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

jinyanwu 2024-12-27 09:44 00 [回复]举报

个人意见,仅供参考:

1、消火栓法兰和下边那个泄水阀所在的管道的法兰应该能对上吧,中间接管这个应该自己制作也可以。就是一节有两个法兰的管道。图集说可以有厂家提供,那在合同阶段就要确定有这个配件了。

2、传动杆同上,根据实际制造即可,没有什么科技含量。

关闭

关闭

手机APP下载