消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

挡烟垂壁高度和疏散高度冲突的问题

    《 建筑防火通用规范》 GB55037-2022 > 第7.1.5条规定:在疏散通道、疏散走道、疏散出口处,不应有任何影响人员疏散的物体,并应在疏散通道、疏散走道、疏散出口的明显位置设置明显的指示标志。疏散通道、疏散走道、疏散出口的净高度均不应小于2.1m。

     而《建筑防烟排烟系统技术标准》 GB51251-2017 >4.6.2 当采用自然排烟方式时,储烟仓的厚度不应小于空间净高的20%,且不应小于500mm;当采用机械排烟方式时,不应小于空间净高的10%,且不应小于500mm。

    也就是说吊顶高度必须在2.6米以上才可以同时满足以上两个条件,而实际上一般走道内设置管线较多并不能完全保证天花下净高就在2.6米以上,也不能说2.6米以下就必须采用格栅吊顶吧,那这个矛盾该怎么解决呢?

SDXDS | 2024-12-09 23:13
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

拾青 2024-12-10 09:57 00 [回复]举报

同问,《建筑防烟排烟系统技术标准》 GB51251-2017 ,4.3.3条 ,1 当设置在外墙上时,自然排烟窗(口)应在储烟仓以内,但走道、室内空间净高不大于3m的区域的自然排烟窗(口)可设置在室内净高度的1/2以上。   如走道净高3.0米,为满足走道两端各开启2.0㎡的面积,挡烟垂壁需要吊至1.5米位置,走道疏散警告就更不够了。  另问,是否走道挡烟垂壁只做500mm就够,但排烟窗有效开启面积可以算1.5米以上的。求大神解释一下?

LHH2737   回复: 拾青2024-12-10 11:21

只做500mm就行,4.3.3条是一条放宽性条文,可以执行,且他并不影响挡烟垂壁高度

0    0 [回复]举报

潘天坤   回复: 拾青2024-12-10 13:15

走道和空间净高不大于3米的场所,自然排烟窗可以设置在空间净高的一半以上,也就是说空间净高一半以上即为有效。对于空间净高受限制的场所,如果还要考虑挡烟垂壁以上则很难满足要求,并且这个内容是有规范依据的

如果走道存在多个防烟分区需要设置挡烟垂壁,挡烟垂壁的不应小于空间净高的20%(采用自然排烟时)且不应小于500毫米,同时要考虑人员疏散通道的高度,可以结合设置开孔率大于25%的通透性吊顶、设置防火门或者实体墙之类的防火分隔(满足疏散的前提下)等综合考虑

0    0 [回复]举报

小唐12321 2024-12-10 10:03 00 [回复]举报

使用活动式挡烟垂壁或者加防火门分隔

潘天坤   回复: 小唐123212024-12-10 13:18

挺多人认为活动式挡烟垂壁下降到底时也应满足疏散净高要求

0    0 [回复]举报

潘天坤 2024-12-10 15:46 00 [回复]举报

目前这类情况比较麻烦,目前没有比较好的方案,看看能否控制住空间净高

如果空间净高受限制,那么需要考虑设置开孔率大于25%的通透性吊顶、设置防火门或者实体墙之类的防火分隔(满足疏散的前提下)


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据 有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准

关闭

关闭

手机APP下载